From what I understand a 25’ 10/3 stranded SOOW wire for power to Hobart 190, with 30 amp breaker is plenty big enough.Specs are 130 amps @ 21.5 volts 30% Duty cycle.This is the wire specs: SOOW 10/3  Cable - SOOW Jacket, 30 Amps, 3 Wire, 600v - Water and Oil Resistant 25’I don’t think 8/3 AGW is needed correct?Just wanted to double check before ordering wire. :-) Cheers, AllenLast edited by abosely; 1 Week Ago at 02:46 AM.
Reply:I would personally choose 8/3 to minimize voltage drop IF the machine is going to be used near it's top-end output frequently.  But 10/3 should be fine if you're welding at low-medium output.

1st on WeldingWeb to have a scrolling sig!



Reply:The 10 is 2 sizes better than the machine needs and will run a machine 2x its size.   Its ideal for this.   I would personally choose 8/3 to minimize voltage drop
Reply:

Originally Posted by Sberry

The 10 is 2 sizes better than the machine needs and will run a machine 2x its size.   Its ideal for this.      How far should a guy go?
Reply:Most 10 gauge is 30 amps.But you to provide more details your welding. Odds are it will work great.My welder takes a 20amp 240 volt and I use 12 gauge wire. Dave Welding is base on duty cycle witch most are lucky to MIG weld 40% time. Stick welding is about 20% of time. Dave

Originally Posted by abosely

From what I understand a 25’ 10/3 stranded SOOW wire for power to Hobart 190, with 30 amp breaker is plenty big enough.Specs are 130 amps @ 21.5 volts 30% Duty cycle.This is the wire specs: SOOW 10/3  Cable - SOOW Jacket, 30 Amps, 3 Wire, 600v - Water and Oil Resistant 25’I don’t think 8/3 AGW is needed correct?Just wanted to double check before ordering wire. :-) Cheers, Allen
Reply:where did you guys learn to size wire and pipe and load demand??????
Reply:OR you could look in the owners manual. Because of duty cycle that welder only requires 14 gauge conductors up to 67 feet from the breaker. 12 gauge would be fine, 10 gauge is a lot of overkill, and 8 gauge is ridiculous.

Miller Multimatic 255
Reply:Like your chart on welder.Dave

Originally Posted by Louie1961

OR you could look in the owners manual. Because of duty cycle that welder only requires 14 gauge conductors up to 67 feet from the breaker. 12 gauge would be fine, 10 gauge is a lot of overkill, and 8 gauge is ridiculous.


Reply:I'm not saying you're wrong. I just personally prefer to do things a wee bit different.
Reply:I like to see guys learn about this to some extent.  They are confused to start with about what makes for safety and concern with the machines, I think we should be realistic.  On another forum,,,, a guy goes in to debt buys a machine from a tool truck on credit.  Modern machine, cant use it till he can save up for a down payment on a chunk of wire he gonna put on his credit card.   Reason,,,,,, wants to be sure he has a circuit with less than 1 volt drop, he has read all the charts, did "research" asked several guys and got a "YOU GO GIRL" kind of answers and thoroughly convinced that this thing comes 12 cord will brown out on anything less than a 6 for his long,,,, 40 ft circuit.     Its kind of sad in its own way,,, all the resource in the world and ends up knowing less than when he started.www.urkafarms.com
Reply:Here is a bit of what I try to imply in this whole scheme, its kind of overlapping but,,,,,,,,,,,,,,,,,,,  I see myself or can look back and have some longer perspective so to speak,,, for example I am replacing some wiring I installed early in my career, same for pipe and doing remans and look back at many of the line items I thought were so crucial along my learning curve.  I see where my understanding was incomplete to some extent and still is,,, I just dont care now,, but where I really missed some stuff that real masters truly understood.   Its as much the "nature " of it as exact science.     I look at my master plumma bud, lic holder 50+ years  still use the same 1/2 steel line he install back then as well as the same 5 hp comp.   My neighbor the every lic you can hold and give a free wire to still has his buzzer connected to 15 ft of 10 cable he hooked it to 45 years ago.www.urkafarms.com
Reply:Not that it couldnt be done better but they really understand demand and know any more wont make it any better.    Its ok for hobby types etc but when it comes to actual sincere demand questions would prefer to be adequate and extrapolate from there.   I rarely follow minimums, have never wired a 210 with 14 but found out they run just dandy with a 12 at a reasonable length.Last edited by Sberry; 1 Week Ago at 12:52 PM.www.urkafarms.com
Reply:Thats a big wire for a short distance, really depends on are you welding at near max amps for long time?We've done so much, for so long, with so little. Were now qualified to do anything with nothing !
Reply:

Originally Posted by welding1

Thats a big wire for a short distance, really depends on are you welding at near max amps for long time?
Reply:

Originally Posted by albrightree

You can start with the NEC code book, but most people don't carry it with them all the time. I often this handy reference book from my tool box :

The Pocket ref is pretty handy it has so much in there about steel pipe and tubing, hydraulic ram capacities, area and zip codes, radio alphabet (ie Whiskey,Tango,Foxtrot, ) Morse code, Floor joist spans (wood) and so much more.To the original poster, yes #10 at 25FT should be fine.
Reply:

Originally Posted by Sberry

Its not a wrong thing but why panic a guy when he is trying to get a good grip, next guy is gonna say he has to have a 6.
Reply:It’s good to get more information about subject, especially with explanations like have been given here.Not needed but in some situations (like running machine at max output a lot) can have some advantages.But good to know that 25’ of 10/3 for the Hobart 190 is a couple steps over what Hobart recommends. Appreciate the input.Have 25’ of the above wire arriving Tuesday. Cheers, Allen
Reply:

Originally Posted by albrightree

The Pocket ref is pretty handy it has so much in there about steel pipe and tubing, hydraulic ram capacities, area and zip codes, radio alphabet (ie Whiskey,Tango,Foxtrot, ) Morse code, Floor joist spans (wood) and so much more.
Reply:The only purpose of a breaker is to protect the wiring,, you might as well help the breaker do its job.
Reply:

Originally Posted by StandarDyne

Kinda the shop version of Bowditch!I didn't check my copy of the Pocket Reference tables on AWG/voltage drop but one thing regarding welders (or plasma cutters or probably anything the OP is gonna run on an extension cord) is that the NEC allows "derating" the wire based on the fact that the load is going to be intermittent since welders, plasma cutters, etc., have a duty cycle requiring them to pause regularly to let their wiring cool down. These pauses also allow the wire in the circuit (and extension cord) to cool down. See NEC 630 for more:https://www.codebookcity.com/codeart...article630.htm
Reply:I NEVER install anything for what I am doing today,,
Reply:Absolutely correct about the permissible downsizing due to duty cycle. What it doesn't mention, however, is that the same permissible downsizing that aims to keep the wire safe from over-heating, doesn't take into account any consideration for voltage drop going to the machine; it's sole concern is the amperage because that is what heats up the wire. However, welders like high input voltage and they like for it to be steadily fed in.
Reply:

Originally Posted by Sberry

How big a deal is it at 240 to a machine that will run on 220. 208, maybe even 200?
Reply:doesn't take into account any consideration for voltage drop going to the machine; it's sole concern is the amperage because that is what heats up the wire
Reply:10/3 is fine.From what I understand a 25’ 10/3 stranded SOOW wire for power to Hobart 190, with 30 amp breaker is plenty big enough.Specs are 130 amps @ 21.5 volts 30% Duty cycle.This is the wire specs: SOOW 10/3  Cable - SOOW Jacket, 30 Amps, 3 Wire, 600v - Water and Oil Resistant 25’I don’t think 8/3 AGW is needed correct?Just wanted to double check before ordering wire. :-) Cheers, AllenLast edited by abosely; 1 Week Ago at 02:46 AM.
Reply:I would personally choose 8/3 to minimize voltage drop IF the machine is going to be used near it's top-end output frequently.  But 10/3 should be fine if you're welding at low-medium output.

1st on WeldingWeb to have a scrolling sig!



Reply:The 10 is 2 sizes better than the machine needs and will run a machine 2x its size.   Its ideal for this.   I would personally choose 8/3 to minimize voltage drop
Reply:

Originally Posted by Sberry

The 10 is 2 sizes better than the machine needs and will run a machine 2x its size.   Its ideal for this.      How far should a guy go?
Reply:Most 10 gauge is 30 amps.But you to provide more details your welding. Odds are it will work great.My welder takes a 20amp 240 volt and I use 12 gauge wire. Dave Welding is base on duty cycle witch most are lucky to MIG weld 40% time. Stick welding is about 20% of time. Dave

Originally Posted by abosely

From what I understand a 25’ 10/3 stranded SOOW wire for power to Hobart 190, with 30 amp breaker is plenty big enough.Specs are 130 amps @ 21.5 volts 30% Duty cycle.This is the wire specs: SOOW 10/3  Cable - SOOW Jacket, 30 Amps, 3 Wire, 600v - Water and Oil Resistant 25’I don’t think 8/3 AGW is needed correct?Just wanted to double check before ordering wire. :-) Cheers, Allen
Reply:where did you guys learn to size wire and pipe and load demand??????
Reply:OR you could look in the owners manual. Because of duty cycle that welder only requires 14 gauge conductors up to 67 feet from the breaker. 12 gauge would be fine, 10 gauge is a lot of overkill, and 8 gauge is ridiculous.

Miller Multimatic 255
Reply:Like your chart on welder.Dave

Originally Posted by Louie1961

OR you could look in the owners manual. Because of duty cycle that welder only requires 14 gauge conductors up to 67 feet from the breaker. 12 gauge would be fine, 10 gauge is a lot of overkill, and 8 gauge is ridiculous.


Reply:I'm not saying you're wrong. I just personally prefer to do things a wee bit different.
Reply:I like to see guys learn about this to some extent.  They are confused to start with about what makes for safety and concern with the machines, I think we should be realistic.  On another forum,,,, a guy goes in to debt buys a machine from a tool truck on credit.  Modern machine, cant use it till he can save up for a down payment on a chunk of wire he gonna put on his credit card.   Reason,,,,,, wants to be sure he has a circuit with less than 1 volt drop, he has read all the charts, did "research" asked several guys and got a "YOU GO GIRL" kind of answers and thoroughly convinced that this thing comes 12 cord will brown out on anything less than a 6 for his long,,,, 40 ft circuit.     Its kind of sad in its own way,,, all the resource in the world and ends up knowing less than when he started.www.urkafarms.com
Reply:Here is a bit of what I try to imply in this whole scheme, its kind of overlapping but,,,,,,,,,,,,,,,,,,,  I see myself or can look back and have some longer perspective so to speak,,, for example I am replacing some wiring I installed early in my career, same for pipe and doing remans and look back at many of the line items I thought were so crucial along my learning curve.  I see where my understanding was incomplete to some extent and still is,,, I just dont care now,, but where I really missed some stuff that real masters truly understood.   Its as much the "nature " of it as exact science.     I look at my master plumma bud, lic holder 50+ years  still use the same 1/2 steel line he install back then as well as the same 5 hp comp.   My neighbor the every lic you can hold and give a free wire to still has his buzzer connected to 15 ft of 10 cable he hooked it to 45 years ago.www.urkafarms.com
Reply:Not that it couldnt be done better but they really understand demand and know any more wont make it any better.    Its ok for hobby types etc but when it comes to actual sincere demand questions would prefer to be adequate and extrapolate from there.   I rarely follow minimums, have never wired a 210 with 14 but found out they run just dandy with a 12 at a reasonable length.Last edited by Sberry; 1 Week Ago at 12:52 PM.www.urkafarms.com
Reply:Thats a big wire for a short distance, really depends on are you welding at near max amps for long time?We've done so much, for so long, with so little. Were now qualified to do anything with nothing !
Reply:

Originally Posted by welding1

Thats a big wire for a short distance, really depends on are you welding at near max amps for long time?
Reply:

Originally Posted by albrightree

You can start with the NEC code book, but most people don't carry it with them all the time. I often this handy reference book from my tool box :

The Pocket ref is pretty handy it has so much in there about steel pipe and tubing, hydraulic ram capacities, area and zip codes, radio alphabet (ie Whiskey,Tango,Foxtrot, ) Morse code, Floor joist spans (wood) and so much more.To the original poster, yes #10 at 25FT should be fine.
Reply:

Originally Posted by Sberry

Its not a wrong thing but why panic a guy when he is trying to get a good grip, next guy is gonna say he has to have a 6.
Reply:It’s good to get more information about subject, especially with explanations like have been given here.Not needed but in some situations (like running machine at max output a lot) can have some advantages.But good to know that 25’ of 10/3 for the Hobart 190 is a couple steps over what Hobart recommends. Appreciate the input.Have 25’ of the above wire arriving Tuesday. Cheers, Allen
Reply:

Originally Posted by albrightree

The Pocket ref is pretty handy it has so much in there about steel pipe and tubing, hydraulic ram capacities, area and zip codes, radio alphabet (ie Whiskey,Tango,Foxtrot, ) Morse code, Floor joist spans (wood) and so much more.
Reply:The only purpose of a breaker is to protect the wiring,, you might as well help the breaker do its job.
Reply:

Originally Posted by StandarDyne

Kinda the shop version of Bowditch!I didn't check my copy of the Pocket Reference tables on AWG/voltage drop but one thing regarding welders (or plasma cutters or probably anything the OP is gonna run on an extension cord) is that the NEC allows "derating" the wire based on the fact that the load is going to be intermittent since welders, plasma cutters, etc., have a duty cycle requiring them to pause regularly to let their wiring cool down. These pauses also allow the wire in the circuit (and extension cord) to cool down. See NEC 630 for more:https://www.codebookcity.com/codeart...article630.htm
Reply:I NEVER install anything for what I am doing today,,
Reply:Absolutely correct about the permissible downsizing due to duty cycle. What it doesn't mention, however, is that the same permissible downsizing that aims to keep the wire safe from over-heating, doesn't take into account any consideration for voltage drop going to the machine; it's sole concern is the amperage because that is what heats up the wire. However, welders like high input voltage and they like for it to be steadily fed in.
Reply:

Originally Posted by Sberry

How big a deal is it at 240 to a machine that will run on 220. 208, maybe even 200?
Reply:doesn't take into account any consideration for voltage drop going to the machine; it's sole concern is the amperage because that is what heats up the wire
Reply:10/3 is fine.