New to forum, but not new to welding (over 10 years experience.) I just purchased a miller shopmaster 300 that has been completely rebuilt. I just need to know what breaker is needed to run in the electrical panel and also what type of disconnect I will need? I will be hooking it up directly to the disconnect as I will not have to move it around my shop it will stay in one place. It is set up to run on 220v. Any help is appreciated.Manual for the welder based on serial number below. https://www.millerwelds.com/files/ow.../O318A_MIL.pdf
Reply:From the manual you posted. Looks like it requires a 125amp CB/Fuse.

Ed Conleyhttp://www.screamingbroccoli.com/MM252MM211 (Sold)Passport Plus & Spool gunLincoln SP135 Plus- (Gone to a good home)Klutch 120v Plasma cutterSO 2020 benderBeer in the fridge
Reply:ok, what about a quick disconnect? non fused or something like a time delayed fuse and what size? Manual doesn't state what kind.
Reply:2-9. Electrical Service Guide 60 Hz 50 HzInput Voltage 200 230 460 575 220 380 415Input Amperes At Rated Output 105 91.2 45.6 36.4 88.2 51 46.8Max Recommended Standard Fuse Or CircuitBreaker Rating In Amperes 150 125 70 50 125 80 70Min Input Conductor Size In AWG/Kcmil 4 6 8 10 6 8 8Max Recommended Input Conductor Length InFeet (Meters) [116 (35)][103 (31)][271(83)][284(87)][99(30)][194(59)][232 (71)]Min Grounding Conductor Size In AWG/Kcmil 6 ,6, 8, 10, 6, 8. 8Reference: 1996 National Electrical Code (NEC). S-0092J Grid didn't copy well from the service manual But it calls for a 125 amp standard fuse or circuit breaker. This allows operation to 300 amps. You can get away with a smaller service if you stay below 200 amps of welding current. |
|