From a quick websearch I found that a 300 needs about 100 amp breaker or more...Can I run it on a 50 or 75 ampIf I run it low?I have 100 Amp sub to the garageBut I still need lights and tunes... :lol:ThanksMiller 211Hypertherm PM 451961 Lincoln Idealarc 250HTP 221 True Wisdom only comes from Pain.
Reply:I'm running my Airco 300 tig on a 60 amp breaker.Have not tripped it up to 230 amps AC tig.Dave J.Beware of false knowledge; it is more dangerous than ignorance. ~George Bernard Shaw~ Syncro 350Invertec v250-sThermal Arc 161 and 300MM210DialarcTried being normal once, didn't take....I think it was a Tuesday.
Reply:Sure, it will run up until breaker threshold. Make sure you use the right size conductors. Sent from my SAMSUNG-SM-N900A using TapatalkI.B.E.W Electrician and Damn Proud of It !!!! .Virtus Junxit Mors Non Separabit http://www.shrinershospitalsforchildren.org/
Reply:You will only pull 100 Amps from the line when you need that kind of power at the work piece.The worst load is probably AC stick - when you brake the arc.When you TIG, you might have the machine set on 200Amps, but the voltage is more like 15V at the tungsten. That means you only need 15x200 or 3000Watts.Now machines aren't 100% efficient (they get hot) but to output 3000Watts, you only technically need 3000/230 or 13 Amps.I find that when you turn on the machine, the initial rush current (sometimes called inrush current) is noticable. My Dialarc would trip a 30Amp breaker pretty regularly. Once it was started, I could go 250 Amps easy.Con Fuse!Miller Dynasty 350Millermatic 350P-Spoolmatic 30AMiller Multimatic 200Hypertherm PowerMax 1000G3Miller Maxstar 200DX
Reply:Depends if your machine has the PFC option or not.Weld like a "WELDOR", not a wel-"DERR" MillerDynasty700DX,Dynasty350DX4ea,Dynasty200DX,Li ncolnSW200-2ea.,MillerMatic350P,MillerMatic200w/spoolgun,MKCobraMig260,Lincoln SP-170T,PlasmaCam/Hypertherm1250,HFProTig2ea,MigMax1ea.
Reply:Originally Posted by shovelonDepends if your machine has the PFC option or not.
Reply:I run my Sync 250 on a 50 amp breaker and have not tripped it in nearly a year. I run with it set at about 200 amps.Burt _____________________Miller Syncrowave 250Millermatic 211Miller 375 Plasma Cutter Hobart Handler 12010FtDrillBit.com
Reply:Originally Posted by John TI don't know what that is...
Reply:Originally Posted by John TI don't know what that is...
Reply:Originally Posted by shovelonPFC is power factor correction. Every transformer(tranny)tig but Miller included it standard in the build except Miller. It is the surge when striking an arc that trips the breaker, or you can use time-delay fulses like I did for years. I ran my LindeUCC305s for years on 60 amp breakers but even with PFC(which mine did) they recommended 100amp service at 300 amps draw. The bummer with Syncs is that the field install costs much more than ordering with it as a factory option. Think of PFC as a battery backup that continuously needs charging, but feeds stored up current upon surging to prevent early breaker tripping or fuse blowing.
Reply:Originally Posted by John Tsounds like your talking about capacitors....
Reply:Originally Posted by shovelonYep. If there is a large empty space in your cabinet, there is none.
Reply:Man feed that thing some power, find some aluminum, and let it eat Nice doggie Dave J.Beware of false knowledge; it is more dangerous than ignorance. ~George Bernard Shaw~ Syncro 350Invertec v250-sThermal Arc 161 and 300MM210DialarcTried being normal once, didn't take....I think it was a Tuesday.
Reply:Originally Posted by MinnesotaDaveMan feed that thing some power, find some aluminum, and let it eat Nice doggie
Reply:Originally Posted by 7A749Take that sucker to the car wash when it gets warmer out!D
Reply:7a, You need to make a sticky about cleaning machinesEd Conleyhttp://www.screamingbroccoli.com/MM252MM211 (Sold)Passport Plus & Spool gunLincoln SP135 Plus- (Gone to a good home)Klutch 120v Plasma cutterSO 2020 benderBeer in the fridge
Reply:A moderate pressure washing is the best way to clean them up inside, but do it in warm weather and then aim some fans on the open welder for several days to dry it out completely. Make sure it's completely dry before putting power on it again. It will look like new inside. Do a search for posts by 7A749 about cleaning welders. Until it's warm weather, you can vacuum or air gun it out, being careful not to hit or damage any components. If you're going to use the air gun, do it outside.CharleyMiller MM252Miller Bobcat 225NTMiller DialArc HF / DIY Cooler2 Victor O/A TorchsetsMilwaukee 8" Metal SawMilwaukee Dry Cut "Chop" Saw 5 Ton Wallace Gantry Various Grinders, Benders, etc.
Reply:Well there he is. 7A749 himself. Hello Steve. I've been talking about you.CharleyMiller MM252Miller Bobcat 225NTMiller DialArc HF / DIY Cooler2 Victor O/A TorchsetsMilwaukee 8" Metal SawMilwaukee Dry Cut "Chop" Saw 5 Ton Wallace Gantry Various Grinders, Benders, etc.
Reply:Originally Posted by 7A749Uh oh....That may not be a good thing I take it over on Miller?? I lost all my login info when my computer crashed. I emailed the admin there & they said they would reactivate my account. I never heard back & that was awhile ago.Prolly have to join again & contact Andy I guess.For any who question washing welding machines, Cruizer will also verify service centers do it all the time. DUH, the post right above this one... Boy, I'm a retard! |
|