New 175 Plus with Argon and Electrical Questions

[复制链接]

9万

主题

9万

帖子

29万

积分

论坛元老

Rank: 8Rank: 8

积分
293221
发表于 2021-8-31 22:35:35 | 显示全部楼层 |阅读模式
Hey Everyone,I just bought a SP175 Plus for home use. It says the the power core is 50 amp.  I haven't ran wire for it yet and wanted to know it #8/3 with common will be big enough and a 50 amp breaker.  Should I go with #6/3 wire instead?One other.  I use a Syncowave 250TIG at work and I use 100% Argon for Stainless, Mild, and Aluminum.  Can I use pure Argon with good result with a MIG?  Reason for asking is I can get Argon here for....... well, lets say real cheap .Thanks James L.
Reply:you would not want to use strait argon with mig unless you are welding aluminum, your penitration will be slight if any and the arc is not real stable Fire doesn't burn a good Christian !
Reply:I just bought a SP175 Plus for home use. It says the the power core is 50 amp. I haven't ran wire for it yet and wanted to know it #8/3 with common will be big enough and a 50 amp breaker. Should I go with #6/3 wire instead?
Reply:Originally Posted by v8eaterHey Everyone,I just bought a SP175 Plus for home use. It says the the power core is 50 amp.  I haven't ran wire for it yet and wanted to know it #8/3 with common will be big enough and a 50 amp breaker.  Should I go with #6/3 wire instead?
Reply:You do not want to do the bare minimum.   Secondly its not complicated at all to run. Just get a Bi-Pole 50amp break, some 6/3 wire, a NEMA 6-50R receptical and your all set.  Pay no attention to the neutral wire as you really don't need.  Also by a box to house the 6-50 plug and just flush mount it to your wall.  You honestly don't even need a electrician to do the work.  Just be very careful like you would when dealing with any electrical device.  IMO the hardest part of setting up 220 to my back garage was digging the actual trench lol.
Reply:As mentioned above, pure argon is not good for MIG. Best bet is ArgonC02 75/25, unless you're cheap like I am and then you'll use C02. Actually, C02 is getting a bad rap. It's perfectly capable of making great welds, just not as pretty as Argon/C02. The penetration is superb, though. And with argon running $50-$75 a bottle locally, hobby welders like me use C02. A 20# bottle is less than $30 for me and has the same amount of gas output as a 160 cu. ft. cylinder of argon/C02. BTW, I have 10 ga. wire to my 220 VAC line for the Lincoln 175 with a 40 amp breaker and have yet to have a problem. As Sandy says above, input current is around 19-21 amps and 10 ga., handles that nicely. 8 ga. would be ideal and 6 is more than you need, IMHO. I'm not totally cheap, though. On my 250/250 Idelarc TIG/STICK, I have a 60 amp breaker with 6 ga. wire. .Last edited by gnm109; 05-12-2006 at 03:49 PM.
Reply:I have to raise objection to the implication below.    IT is NOT safe to put a 40 amp breaker into a circuit made up of 10 gage wire.   The purpose of the breaker is to protect the branch circuit wiring and thus the structure the wiring is in.   You are close, but as far as the NEC is concerned not there, the wire is undersized for the breaker.ThanksDave Originally Posted by gnm109........BTW, I have 10 ga. wire to my 220 VAC line for the Lincoln 175 with a 40 amp breaker and have yet to have a problem. As Sandy says above, input current is around 19-21 amps and 10 ga., handles that nicely. 8 ga. would be ideal and 6 is more than you need, IMHO.
Reply:Originally Posted by wizardIT is NOT safe to put a 40 amp breaker into a circuit made up of 10 gage wire.   The purpose of the breaker is to protect the branch circuit wiring and thus the structure the wiring is in.   You are close, but as far as the NEC is concerned not there, the wire is undersized for the breaker.
Reply:Originally Posted by MAC702Actually, Article 610 of the NEC would allow this for this welder.  In a residential setting, it might be discouraged by some electricians, and in any case, it should be well-labeled with no chance of someone else using the circuit for something else.
Reply:That said, a 175A welder only needs a 30A circuit.  Where did all this big wire/big breaker talk get started?  It comes with a 50A plug because that is historically a typical welder plug.  Unless you want to allow for future upgrades (not a bad idea), you only need to run 10/2 (plus ground) and install a NEMA 6-50R receptacle.
Reply:Originally Posted by MAC702That said, a 175A welder only needs a 30A circuit.  Where did all this big wire/big breaker talk get started?
Reply:I used to have problem with my miller dial  arc 250 hf(for tig) was wired for 70 amps w/70 amp breaker . it worked , but every time i shut it off , would trip  breaker . I finally went from a zinsco   100 amp box to a challenger 200 amp box , hard wired the miller to a 100 amp breaker , wallah !  no more problems . At the same time i provided 50 amp outlet for the sp 250 lincoln mig, and a couple 20 amp outlets for air compressor ,etc. by the way , my sp250 has an "extension cord" about 30 ft. long 4 conductor #6 , no problems . i know it don't need 4 wire , but it was given to me .
Reply:It should state in your Lincoln book what is required. In my book for my "Miller time" it had a chart and the rating for several examples of how to hook it up. I was so busy with other work, I just called an electrician, talk to him for a few and he hooked it up nicely with nice bent conduit, box and all. Problem is, when you have someone doing work for you, you end up allocating other tasks so I ended up with more 8 footer lights in my shop. John -  fabricator extraordinaire, car nut!-  bleeding Miller blue! http://www.weldfabzone.com
Reply:Originally Posted by MAC702That said, a 175A welder only needs a 30A circuit.  Where did all this big wire/big breaker talk get started?  It comes with a 50A plug because that is historically a typical welder plug.  Unless you want to allow for future upgrades (not a bad idea), you only need to run 10/2 (plus ground) and install a NEMA 6-50R receptacle.
Reply:As long as it's an INFORMED decision, he can run #6 wire, sure.  But actually, if he was "getting by" he could run #12 for that welder, if he used a receptacle that would hold a wire that small.  #10 is more than adequate for that machine.  For someone to recommend larger, they should include that it would be for future upgradability, and that it provides no measurable benefit to this installation.  Don't mean to step on any toes.
Reply:Hey everyone, sorry for not getting back to you all sooner.  Haven't been off from work long enough to run wire yet.I did decide to go ahead and get the 6/3 with a common. I know...one wire too many, but I'll have it if I need it.  It was only .10 cents a foot more than 8/3.  So as mentioned above I want have to worry later if I get some that requires more amps.  Our next camper will probally be 50 amps anyway.Hopefully, I will get wire ran next weekend and pick up a 75/25 Argon/co2 also.Thanks for all the help, James L.
Reply:Originally Posted by v8eaterI did decide to go ahead and get the 6/3 with a common. I know...one wire too many, but I'll have it if I need it...  Our next camper will probally be 50 amps anyway.